Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

125-ft 6 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 125-ft 6 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.4
214

work for iowa code for electric range?


It satisfies the NEC for a range circuit, but whether it can be used in Iowa is dependent on Iowa codes. Check with your local authority having jurisdiction on whether they allow the use of NM-B cable. 6-3 NM-B cable can be protected with a 50 amp or maximum of a 60 amp breaker. If you need a 40 amp circuit (even at 72 feet), I'd use 8-3 NM-B cable.

Was this Answer Helpful ?