Why won't these breakers work in the homeline panels 20/40??
1
It is not clear what the catalog number is for the load center or application. The maximum HOMELINE branch circuit breaker is 50 ampere (single pole) and 200 ampere (two pole). NOTE: The maximum branch breaker cannot exceed the ampere rating of the load center. The two pole, 150-200 ampere, branch breakers are restricted for use in HOMELINE load centers rated 150 ampere or greater, and they take up four spaces in the load centers. NOTE: The branch breakers are differentiated from the old replacement main breakers by using suffix BB (example: HOM2150BB) Regards, Customer Care