Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

Electrical Box

REDDOT Electrical Box

4.6
95

Does ths product meet code requirements for outdoor use


This product does not comply with NEC code 210.8 (A)for GFCI protection which is required for outdoor electrical outlets. Per 210.8(A)(3), all 15A and 20A, 125V receptacles outside of a dwelling unit, including receptacles installed under the eaves of roofs, shall be GFCI-protected. The only exception to this rule is that GFCI protection is not required for fixed electric snow melting or de-icing equipment receptacles that are not readily accessible and are supplied by a dedicated branch circuit in accordance with 426.28

Was this Answer Helpful ?

Yes, I would say so. But your local code may be more stringent. Would need to ask local building inspector to be sure, if not than just return it to the store after you get an answer.

Was this Answer Helpful ?

Yes, this box is approved for outdoor use.

Was this Answer Helpful ?