Does this valve conform with ASSE 1003 as be the Ohio Plumbing Code?
1
As I understand your question: Where water pressure within a building exceeds 80 psi (552 kPa) static, an approved water-pressure reducing valve conforming to ASSE 1003 or CSA B356 with strainer shall be installed to reduce the pressure in the building water distribution piping to not greater than 80 psi (552 kPa) static. Standards Compliance • ASSE® Listed 1003 • IAPMO® Listed • CSA® Certified • NSF® Listed - Standard 61, Annex G* • Certified to NSF/ANSI 372* by IAPMO R&T *(0.25% MAX. WEIGHTED AVERAGE LEAD CONTENT) Max. working water pressure (1/2” - 1-1/4”) 400 psi Minimum inlet pressure = 80 psi as per UPC Code Max. working water pressure (1-1/2” - 2”) 300 psi Max. working water temperature 140°F Reduced pressure range (1/2” - 1-1/4”) 15 to 75 psi Reduced pressure range (1-1/2” - 2”) 25 to 75 psi Factory preset 50 psi