Utilitech 30 -Amp 120-volt Industrial Round RV power outlet Receptacles , Black
I want to install this outlet apx. 130' from breaker box. Would you recommend UF-B 10-3 or 8-3? Something else? Would be powering a KZ Sportsman 19BHS
2
NEC code for voltage drop that distance it’s 8-3 AWG. 2x130’x30ampx12.9(resistance of awg) / 6.6 (v.drop permitted= 15245 c.mils or 8awg.
Was this Answer Helpful ?I would suggest 6 AWG rather than 8. DEFINITELY NOT 10AWG!! The 8 would be fine up to 100' so I highly suggest you honestly measure the exact length and decide if you want to stretch out the RV cord as that may allow a shorter length for your outlet.