Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

30 -Amp 120-volt Industrial Round RV power outlet Receptacles , Black

Utilitech 30 -Amp 120-volt Industrial Round RV power outlet Receptacles , Black

4.8
1035

Should I use 6/3 or 8/3 wire? Also, we have a 50 amp circuit breaker, is that correct?


You can use the 50 amp breaker with 6-3 NM-B cable or a 40 amp breaker with 8-3 NM-B cable. Check your range installation instructions to see what amperage is recommended for your range, but most require a 40 amp circuit. You have selected the wrong receptacle though. Since 1996 the NEC has required a 4-wire circuit with a 4-wire receptacle and 4-wire/prong range cord and plug.