Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

Universal Whole Home 25-kA Indoor and outdoor Surge protective device

Square D Universal Whole Home 25-kA Indoor and outdoor Surge protective device

4.6
97

Can I hook this directly to the 200amp main or do I have to use a separate 30amp breaker


Hi batman6969, Yes it can be connected directly into the bus of your panel. or the load end of your Main breaker. But the major consequence for this installation is in replacing the SPD. The whole panelboard would have to be de-energize the whole panelboard just to disconnect and replace the SPD. If this is a concern then use a separate branch breaker as disconnect for the SPD device. We recommend a 2 pole 20A instead of 30A breaker. Warm Regards, Schneider Customer Care