Will this interlock kit Square D Homeline Kit Model #HOMCGK2C fit any of these panel as sold at Lowes. Square D Homeline ##HOM2040L125PC?
1
Hello Tony, Part #HOMCGK2C CANNOT be used with HOM2040L125PC since it is a 125A load center. This kit is only for Homeline load center that utilizes a QOM2 frame main circuit breaker 150 - 225 Amp MAX. Kit part number HOMCGK2C is compatible with any Series S, NEMA Type 1 (indoor) and Series S1, NEMA Type 3R (outdoor), convertible Homeline main breaker load center that utilizes a QOM2 frame main circuit breaker (150 - 225 Amp MAX.). It interlocks the QOM2, 2-pole main circuit breaker with a HOM 2-pole (15-125 Amp MAX.) branch circuit breaker. The branch breaker used as the back-fed generator breaker cannot exceed 125 Amp MAX.. Kit includes a retaining kit for the HOM branch breaker used as the back-fed breaker for the generator. NOTES: a) Series S and Series S1 convertible Main Lug load centers, that meets the description provided above, could also be used by converting the load center to a Main Breaker device using the QOM2 Main Breaker. b) Not applicable for the HOM60120M200PC or HOM60120L225PC, a generator interlock kit is NOT available for the 60 space Homeline load centers. Regards, Schneider Electric Customer Care