Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

QO 200 Amp Single phase (120V/240V) Fusible Outdoor General-duty Enclosed Circuit Breaker Disconnect

Square D QO 200 Amp Single phase (120V/240V) Fusible Outdoor General-duty Enclosed Circuit Breaker Disconnect

4.5
17

This will be installed between the meter and the circuit breaker box so does this box get grounded to a driven ground rod?


Yes

Was this Answer Helpful ?

Thank you for inquiry. Please confirm installation code requirements with local authorities having jurisdiction.

Was this Answer Helpful ?

This disconnect has the first OCPD so this is where the neutral gets grounded to at least one ground rod and to the metallic water piping within 5 feet of where the piping enters the building. The neutral bus must be bonded to the metal can. The feeder to the inside subpanel must be 4 wires and the neutral must be isolated from ground. You'll need to purchase and install a ground bar kit for the inside subpanel.

Was this Answer Helpful ?