Read All Questions & AnswersIs this breaker ok for a dryer with 10/3 wire? Is this the same as having a 30amp double pole with a common trip between the two? Just looks different
1
Hi Trish, Cable range for QO230CP is 14–8 Al / Cu or (2) 14–10 Cu, both poles will trip, which is not the same as having two 1-pole breakers tied together, in which case each breaker will trip individually. Sincerely, Schneider Electric Customer Service