does it need to be bonded and can neutrals and grounds be on the same bar in the main panel?
1
Hello Shawn. Sharing neutrals with grounds and visa versa, depends upon the application in which the load center is used. If the load center is installed as the point of Service Entrance, the neutral is field bonded to the enclosure so any unused neutral / ground terminals may be used to terminate either wires. They are already commonly connected as the Service Entrance wiring standards dictate for load centers and panelboards. If the load center is installed as a sub-panel, the neutral is isolated and not bonded to the enclosure's ground therefore all branch ground wires must be terminated into an equipment ground bar and neutrals to the neutral bar only. Warm regards. Schneider Electric Customer Care