Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

23 Terminal Aluminum Ground bar kit

Square D 23 Terminal Aluminum Ground bar kit

4.8
215

does it need to be bonded and can neutrals and grounds be on the same bar in the main panel?


Hello Shawn. Sharing neutrals with grounds and visa versa, depends upon the application in which the load center is used. If the load center is installed as the point of Service Entrance, the neutral is field bonded to the enclosure so any unused neutral / ground terminals may be used to terminate either wires. They are already commonly connected as the Service Entrance wiring standards dictate for load centers and panelboards. If the load center is installed as a sub-panel, the neutral is isolated and not bonded to the enclosure's ground therefore all branch ground wires must be terminated into an equipment ground bar and neutrals to the neutral bar only. Warm regards. Schneider Electric Customer Care