Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

50-ft 8 / 2 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 50-ft 8 / 2 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.7
136

Can I use this for 220v 40 amp ckt for a electric stove


Hello, thank you for your question. This answer will require a more technical response. Please reach out to our technical team at cabletechsupport@southiwre.com for a detailed explanation of your question.

Southwire Tools Support Was this Answer Helpful ?

First, you don't have 220 volts, you have 240 volts. You do not need 240 volts for an electric stove, it requires a 120/240 volt circuit which means you need 2 hot insulated conductors, 1 neutral insulated conductor and 1 grounding conductor so the answer is "NO", you cannot use this 8-2 NM-B cable. You should use 8-3 NM-B cable to get the required 4 conductors for your electric stove. You'll also need a 4-prong range receptacle and a 4-wire cord/plug for the range since electric ranges do not come with a cord.