Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

50-ft 10 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 50-ft 10 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.6
330

Can I use to hook up my stove?


Hello, and thank you for your question. No — 10/3 NM‑B is only rated for a 30‑amp circuit and is not suitable for most electric stoves, which typically require a 40‑ or 50‑amp 240‑V circuit using 8/3 or 6/3 NM‑B depending on the appliance. If you have any additional questions or feedback, please reach out to us at consumersupport@southwire.com.

Southwire Tools Support Was this Answer Helpful ?

Most electric ranges require a 40 amp circuit using 8-3 NM-B cable and some require a 50 amp circuit using 6-3 NM-B cable. This 10-3 NM-B cable must be protected at no more than 30 amps.

Was this Answer Helpful ?

I don’t recommend using 10/3 for anything above 30 Amps. Most stoves are 50 Amp requiring at least 8/3. I prefer to go up one size and use 6/3.

Was this Answer Helpful ?