Southwire 250-ft 12 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )
Can this wire be buried in conduit
2
No! NM-B cable can only be used in indoor dry locations. Outdoor and underground locations, even in conduit, are both classed as wet locations by the NEC. Since you are using conduit there is no need to use a cable at all, I'd pull in separate THHN/THWN conductors.
Was this Answer Helpful ?Type NM-B cable is approved for use in dry locations only. We Recommend using type UF-B cable for a burial or underground application.
Was this Answer Helpful ?