Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

250-ft 12 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 250-ft 12 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.7
82

Can I use this to feed a swimming pool panel from my main electrical panel? It would be buried underground in schedule 40 conduit...


Hello, thank you for your question. This answer will require a more technical response. Please reach out to our technical team at cabletechsupport@southiwre.com for a detailed explanation of your question.

Southwire Tools Support Was this Answer Helpful ?

No! NM-B cable can only be used in indoor dry locations. Outdoor and underground locations, even in conduit, are both classed as wet locations by the NEC. Since you are using conduit there is no need to use a cable at all, I'd pull in separate THHN/THWN conductors.