Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

250-ft 10 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 250-ft 10 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.6
328

can this be used to hook up a 220 hot tub?


Hello, thank you for your question. This answer will require a more technical response. Please reach out to our technical team at consumersupport@southwire.com for a detailed explanation of your question.

Southwire Tools Support Was this Answer Helpful ?

You do not have 220 volts, you have 240 volts. If the hot tub requires a 30 amp circuit this can be used to feed the spa disconnect. It cannot be used between the spa disconnect and the hot tub as this feeder is required to have an insulated grounding conductor and NM-B cable has a bare grounding conductor. Mot hot tubs require either a 50 amp or 60 amp GFCI protected 120/240 volt source.

Was this Answer Helpful ?