Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

250-ft 10 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 250-ft 10 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.6
328

Can this be used for an electric stove


Hello, and thank you for your question. No — 10/3 NM‑B is only rated for a 30‑amp circuit and cannot be used for an electric stove, which typically requires a 40‑ or 50‑amp 240‑volt circuit using 8/3 or 6/3 NM‑B depending on the appliance. If you have any additional questions or feedback, please reach out to us at consumersupport@southwire.com.

Southwire Tools Support Was this Answer Helpful ?

No! Most electric ranges require a 40 amp 120/240 volt circuit which can be installed using 8-3 NM-B cable and some electric ranges require a 50 amp 120/240 volt circuit that can be installed using 6-3 NM-B cable. The 10-3 NM-B cable you selected must be protected at no more than 30 amps.