Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

250-ft 10 / 2 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 250-ft 10 / 2 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.6
446

Can i run 50ft of 12/2 240v @20amps


Hello, and thank you for your question. Yes — a 12/2 copper NM‑B circuit is rated for 20 amps, and running it 50 ft on 240V at 20A is acceptable, as the NM‑B ampacity for 12 AWG is 20A per NEC. If you have any additional questions or feedback, please reach out to us at consumersupport@southwire.com.

Southwire Tools Support Was this Answer Helpful ?

Is this a 20 amp circuit or a 20 amp load? If a continuous load you'll have to use 10-3 NM-B cable as long as the entire circuit is indoors in a dry environment. If the circuit is outside I'd suggest you use UF-B cable.