Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

250-ft 10 / 2 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 250-ft 10 / 2 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.6
446

Is 10/2 wire ok for electric range


Hello, and thank you for your question. No — 10/2 NM‑B cannot be used for an electric range, because modern ranges require a 240‑V 4‑wire circuit (two hots, neutral, and ground), while 10/2 provides only one hot, one neutral, and a ground. If you have any additional questions or feedback, please reach out to us at consumersupport@southwire.com.

Southwire Tools Support Was this Answer Helpful ?

NO! Not only is 10-2 NM-B cable too small, but it is also 2 conductors short of what is required for an electric range. Most electric ranges require a 40 amp circuit which would require 8-3 NM-B cable and some ranges require a 50 amp circuit which would require 6-3 NM-B cable. You MUST have two insulated hot conductors, one insulated neutral conductor and one grounding conductor in the circuit.