Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

25-ft 10 / 2 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 25-ft 10 / 2 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.6
446

Can you use this for a kitchen stove


Southwire 10/2 NM‑B cable is not suitable for most kitchen stoves, because standard electric ranges typically require a 120/240V, 40–50 amp circuit, which calls for 6/3 or 8/3 range‑rated cable—not 10/2. Please let us know if you need help in any other way by contacting us at consumersupport@southwire.com.

Southwire Tools Support Was this Answer Helpful ?

No, for two reasons. 10-2 NM-B cable only has 2 insulated conductors and a kitchen electric range needs 120/240 volts and that requires 3 insulated conductors and 1 ground conductor (bare or green insulated). The second reason is that 10-2 NM-B cable must be protected at 30 amps and most ranges require a 40 amp circuit, a few require a 50 amp circuit. I would use 8-3 NM-B cable with a 40 amp 2 pole breaker.

Was this Answer Helpful ?