Southwire 25-ft 10 / 2 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )
Can this be used on a 50 amp rv recptacle
3
No, 10-2 NM-B cable is only rated at 30 amps. You could use 6-2 NM-B cable if the 50 amp circuit is 120 volts and if the wire is installed indoors.
Was this Answer Helpful ?No, 10 gauge wire is rated to 30 amps, 50 requires 6 gauge wire. Also, NM-B is not rated for outdoor (wet) use.