Southwire 15-ft 14 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )
Is this wire suitable for underground burial?
4
Hello! Your inquiry is best handled by our specialized staff. Please email us at consumersupport@southwire.com, and we'll be happy to assist.
Was this Answer Helpful ? No, NM-B cable is for indoor dry locations only. Outdoor and underground use, whether direct buried or in conduit, are classed by the NEC as wet locations. For direct burial you should use UF-B cable buried 24" deep. For buried conduit you can used THHN/THWN-2 conductors. The conduit must be 18" deep.
Was this Answer Helpful ?no this wire is not suitable for underground burial. You need a wire marked as UF for direct underground burial
Was this Answer Helpful ?No. You need wire specifically rated for burial