Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

125-ft 6 / 2 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 125-ft 6 / 2 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.7
104

can this cable be put in a pvc underground conduit?


Great question! No — 6/2 NM‑B (Romex SIMpull) cannot be installed in PVC underground conduit. NM‑B is not rated for wet locations, and the NEC considers all underground conduit to be a wet environment, even if it appears sealed. For underground runs, you must use UF‑B, USE‑2/URD, or Mobile Home Feeder, depending on your installation. Please let us know if you need help in any other way by contacting us at consumersupport@southwire.com.

Southwire Tools Support Was this Answer Helpful ?

No, this 6-2 NM-B cable is for use in indoor dry locations only. Outside conduits, whether underground or above ground, are classed as wet areas. A better choice would be either separate THWN conductors in conduit or direct burial 6-2 UF-B cable.