Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

100-ft 14 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 100-ft 14 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.8
541

can this be used for a drier outlet ?


Hello, and thank you for your question. 14/3 NM‑B is too small for a dryer; use 10/3 NM‑B for a proper 30‑amp dryer circuit. If you have any additional questions or feedback, please reach out to us at consumersupport@southwire.com.

Southwire Tools Support Was this Answer Helpful ?

No, not only are the conductors too small, there are not enough conductors for an electric dryer circuit. A dryer circuit must have 4 wires; one Blk, one Red, one Wht and one bare ground and they all must be 10 AWG and protected at 30 amps by either a 2 pole 30 amp breaker or 30 amp fuses.

Was this Answer Helpful ?

No, not large enough for electric dryer

Was this Answer Helpful ?

no, only good for a 15 amp circuit

Was this Answer Helpful ?

yes

Was this Answer Helpful ?