Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

100-ft 10 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 100-ft 10 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.6
328

Can be use for electric range?


Hello, and thank you for your question. No — 10/3 NM‑B is not suitable for an electric range. If you have any additional questions or feedback, please reach out to us at consumersupport@southwire.com.

Southwire Tools Support Was this Answer Helpful ?

No, most electric ranges require a 40 amp circuit and some require a 50 amp circuit. 10-3 NM-B cable must be protected at no more than 30 amps.

Was this Answer Helpful ?