Southwire 100-ft 10 / 3 / Romex SIMpull Solid Indoor CU NM-B W/G Individual pack ( By-the-roll )
Can be use for electric range?
2
Hello, and thank you for your question. No — 10/3 NM‑B is not suitable for an electric range. If you have any additional questions or feedback, please reach out to us at consumersupport@southwire.com.
Was this Answer Helpful ? No, most electric ranges require a 40 amp circuit and some require a 50 amp circuit. 10-3 NM-B cable must be protected at no more than 30 amps.