Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

75-ft 8 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 75-ft 8 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.6
138

Need to run approx 100 feet underground to my deck to power a sauna... 110 20 amp ... what size and kind of wire


Hi, happy to help! For a 110V / 20‑amp sauna circuit run 100 ft underground, you’ll want to use 12/2 UF‑B copper (direct‑bury rated) or THHN in PVC conduit, not NM‑B (Romex), which is indoor‑only and cannot be used underground. If we can help in any other way, please reach out to us at consumersupport@southwire.com.

Southwire Tools Support Was this Answer Helpful ?

8-3 NM-B cable cannot be used. NM-B cable is not allowed to be used either outdoors or underground. I'd use #12 THHN/THWN-2 conductors in PVC conduit.

Was this Answer Helpful ?