Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

75-ft 8 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 75-ft 8 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.6
138

I need to run 8 ga 3 conductor wire in PVC conduit to a workshop in my back yard . What is the correct spec wire to use?


Hello, thank you for your question. This answer will require a more technical response. Please reach out to our technical team at cabletechsupport@southiwre.com for a detailed explanation of your question.

Southwire Tools Support Was this Answer Helpful ?

You need 4 conductors to feed a subpanel. The NM-B cable where you posted your question cannot be used, NM-B cable can only be used in indoor dry locations and outside/underground conduit is classed by the NEC as a wet location. You could use 3 - #8 THHN/THWN-2 conductors with a #10 ground fed from a 40 or 50 amp 2-pole breaker, but I would recommend you use 3 - #6 THHN/THWN-2 conductors with a #10 ground fed from a 60 amp 2-pole breaker.