Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

75-ft 6 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 75-ft 6 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.4
214

Can this wire be used to run a load center in a converted garage to apartment?


Hello, thank you for your question. This answer will require a more technical response. Please reach out to our technical team at consumersupport@southwire.com for a detailed explanation of your question.

Southwire Tools Support Was this Answer Helpful ?

IF the garage is attached this 6-3 NM-B cable can feed a subpanel for the apartment. It must be protected at no more than 60 amps. IF the garage is detached this 6-3 NM-B cable will not work because it is only approved for dry locations. Outside and underground conduits are classes as wet locations.

Was this Answer Helpful ?

The wire can only be used indoors, and is rated for 50 Amps.