Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

75-ft 6 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

Southwire 75-ft 6 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )

4.4
214

can this be used for hot tub hookup?


Hello, thank you for your question. This answer will require a more technical response. Please reach out to our technical team at cabletechsupport@southiwre.com for a detailed explanation of your question.

Southwire Tools Support Was this Answer Helpful ?

This would certainly work to feed either a 50 amp or 60 amp spa panel, but between the spa panel and the hot tub the NEC requires an insulated ground wire and this NM-B cable only has a bare ground so this cable could not be used.

Was this Answer Helpful ?

Yes, this is what I have used in the past and it worked great.