Southwire 75-ft 6 / 3 / Romex SIMpull Stranded Indoor CU NM-B W/G Individual pack ( By-the-roll )
can this be used for hot tub hookup?
3
Hello, thank you for your question. This answer will require a more technical response. Please reach out to our technical team at cabletechsupport@southiwre.com for a detailed explanation of your question.
Was this Answer Helpful ? This would certainly work to feed either a 50 amp or 60 amp spa panel, but between the spa panel and the hot tub the NEC requires an insulated ground wire and this NM-B cable only has a bare ground so this cable could not be used.
Was this Answer Helpful ?Yes, this is what I have used in the past and it worked great.