Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

30-Amp-Space Generator Power Inlet Box

Reliance 30-Amp-Space Generator Power Inlet Box

4.8
162

I plan to purchase a portable 8000 watt generator with a 30 amp outlet. (1) Will the 8000 watt be a problem? (2) Is 10/2 or 10/3 wire required?


The 8000 Watts of Power with a 30 Amp-Outlet should Not be a problem. Typically these 8K Watt (Continuous) 10K Watt (Peak/Starting) have a 30 Amp Breaker for the L14-30R Receptacle on the Distribution Panel of the Generator. So while the Generator can theoretically supply 8000 Watts of Power (32-Amps), this 30 Amp Breaker limits the Power Output to 7500 Watts at this Receptacle. You can also use the 110/20v 20-Amp Outlets and/or the 50-Amp 120/240 4-Prong Outlet, if you wish to push the Power-Output to the 8000 Watt Limit. And if you plan to use the Generator for both 120/240 Volts (Single/Split-Phase), then you will require the "10/3" Wiring. Be advised that "10/3" Wiring equates to three (3) Conductors, (typically Black & Red for Line-Power, White for Neutral/Return for 120-Volts), and the "NON-Conductor" Green or Bare Copper for Safety-Ground. Hope this helps.