Does it need a magnetic starter? What size circuit breaker is required?
2
It does not need a magnetic starter. I mounted mine on rubber vibration pads and bolted it to the floor loosely mainly to avoid it walking. I also mounted a 3 stage inline filter on 1/2 rubber flex hoses. Quincy does not specify the circuit breaker size but I can tell you the motor is rated at 21 amps and it pulls 20.5 amps running at 241 volts. I hooked mine up to a 40 amp breaker with 8 awg wire just to not get voltage drop at startup but I suspect you would be fine with a 30 amp breaker. The people that say it needs 50 amps are just wrong. The internal wiring is only 10 gauge which is rated for 30 amps.
Was this Answer Helpful ?double pole 30 amp breaker. Air pressure regulator/water filter/oiler(should your tools require it)