will it run a heat pump if nothing else?
4
Depends on tonnage and lock rotor compressor amps (startup in rush). Look at the data tag on your condenser - multiply compressor LRA times 240 and this is your startup wattage (plus condenser and indoor fan motors). Multiply compressor RLA times 240 and this is your run load amps. Both need to be under the MAX wattage output for your generator.
Was this Answer Helpful ?Without knowing the specifics of the device you intend to power, no recommendation can be made.
Was this Answer Helpful ?As we are unfamiliar with the output power requirements of your personal heat pump, we would recommend contacting a certified installer in your local area to ensure that you are utilizing the appropriate parts and products for your backup power needs. For help locating a certified party closest to you, please contact us directly at 888-GENERAC (436-3722).