Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

QO 15-amp/15-amp 1 -Pole Tandem Circuit Breaker

Square D QO 15-amp/15-amp 1 -Pole Tandem Circuit Breaker

4.7
637

Are these breaker rated for aluminum wire? The one I have shows the abbreviation CU on it. No AL anywhere.


The Square D QO series circuit breakers are rated for either copper or aluminum wire, but the aluminum termination must be properly made.

Was this Answer Helpful ?

I don't know what type of breaker you have, but the problem with aluminum wire is reaction with dissimilar metals are connected (aluminum wire to copper wiring of the breaker) the metals break down and can cause overheating and arching, hence possible fire. There is a chemical you can put generously on the metals to lessen the affect so if you do keep the aluminum wire, use the compound. Aluminum was used for a brief time many decades ago, and if possible, you should remove it and put in proper sized insulated romex in your house instead. As far as the amperage, this is not a factor of the metals, but the amount of current the breaker and wire can handle. 15 amp breaker goes with 14 gauge wire. This is typical residential wiring circuit. 20 amp breaker goes with 12 gauge wire. This a minimum circuit size in commercial, and often microwave circuits or garage circuits in houses, or any other areas you might need more than 15 amps. This is assuming a 120 volt circuit (single pole) not 240 volt.

Was this Answer Helpful ?

The wire range for the lug on a QO120 and QO120CP is One #14-8 AL /CU or two #14-10 CU.