Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

Homeline 30-amp 2 -Pole GFCI Circuit Breaker

Square D Homeline 30-amp 2 -Pole GFCI Circuit Breaker

4.8
1291

Would this be a good breaker for an 240V 30A EV charger?


Hello Crusher 76. If you are using the HOM250GFI in a 240Vac system without load neutral, yes it can be used. Simply terminate the two hot wires on the breaker and leave the neutral lug unattached. The pigtail wire on the breaker should still be connected to the neutral bar in the panel - this is required to power the push to trip/test feature which verifies the status of the ground fault electronics. Warm regards. Schneider Electric Customer Care