I'm changing my 15 amp square D gfi to a none gfi 20 amp square D circute braker .
3
You have two issues. One is that the circuit may be required to be GFCI protected, but you haven't mentioned what is on the circuit. The second issue is upgrading the overcurrent protection from 15 to 20 amps. You cannot do this without upgrading the wiring from #14 to #12. Not upgrading the wiring to meet the 20 amps of the breaker would be a serious code violation and a hazard.
Was this Answer Helpful ?Your current single pole GFI has two screws and a neutral pigtail. One screw is the "hot" connection, the other screw is the neutral connection. The pigtail is then connected to the neutral bar to the panel. If you replace this breaker with a "regular" breaker, the regular breaker has one screw for the "hot" connection. The neutral for that breaker is connected directly to the neutral bar, so that neutral wire you originally had connected to the GFI breaker will now be connected to the neutral bar instead.
Was this Answer Helpful ?No problem with replacing a GFCI with a non GFCI if you are sure that no receptacles on the circuits require GFCI protection. You do have a problem with replacing a 15 amp breaker with a 20 amp breaker. Breakers are sized to the gauge wire used in the circuit. 15 amp breaker will protect 14 ga wire. 20 amp will protect 12 ga wire. This is providing this is 120 volt. If you use a breaker larger than the wire like using 20 amp breaker with 14 ga wire, you increase the possibility of the wire overheating and causing a fire. Its best to replace breakers with the same amperage.