Prices, Promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.

QP 15-amp 1 -Pole Standard trip Circuit Breaker

Siemens QP 15-amp 1 -Pole Standard trip Circuit Breaker

4.8
1145

Is this circuit breaker rated for a 4500 Watt hot water heater with a red, a black and ground wire?


250watt

Was this Answer Helpful ?

For a 4500 watt electric water heater you can use either a 25 amp 2-pole or a 30 amp 2-pole breaker. The QP230 breaker would be fine for your water heater if you have a Siemens panel or any other panel that is approved to use a Siemens breaker. Consult the label inside the panel door if you have a panel other than a Siemens for a list of manufacturer's breakers approved for use in the panel.

Was this Answer Helpful ?

Yes it is. Now there is one other thing to look at and that is the wire gauge running to the water heater. Is it 10 gauge? If so than this would be the correct size breaker for that wire. Remember the breaker is there to protect the wire and 10 gauge is rated for a 30 amp breaker. Hope this helps